Hi there!
I had a power outage a couple of weeks ago and I had an eye on the 4 rectifiers (MPR25)... They went over 28Amps each one and the power outage lasted only 12 minutes.
The battery backup is designed for 2 hours.
The 8 Batteries (2 banks of 12V-75AH ea.) are OK as they were tested the same week.
Floating voltage is 54V and consumption in normal condition is 54Amp (just coincidence!).
Is it normal that the MPR25s supply 28Amps (even for short periods) or can they get damaged?
Do I have to buy another MPR25 just for these events or our design is correct?
Do you think there is a problem with design of the Nortel rectifier in terms of battery charger?
TIA
Jaime G.