Personally, I would put a separate conduit in for the riser for fire alarm.
Some good points have been made though, assuming it is power limited, I don't believe it is a code violation to run it in the same raceway, it is limited energy wiring as is the date cabling. Again, I don't think the NEC prevents it. That being said, I spent 8 years in the fire service, and the AHJ from fire department side could reject it and make you move it, even though the NEC allowed the installation. We do the entire range of installations, the only time I would intermingle fire alarm would be in a gutter situation where we had gutter feeding several limited energy systems (phone, data, HVAC, fire alarm, etc) and it could be neatly bundled and separated.
Conventional fire alarm systems are just going to be dumping 24vdc on the wire for the most part, and that generally isn't going to cause you a problem in close proximity to data cabling, also there is very little current flow on the fire alarm wire (normally).
Addressable systems with a data circuit are almost always (always when i do them) run on a shielded pair, so the data is contained on the wire inside the shield and not noisey to the surroundings. More importantly it keeps outside noise from interfering with the integrity of the life safety system (more important anyway).
We often (usually) spray paint the boxes and cover plates, and some exposed pieces of conduit red for fire alarm installations, making it quick and easy to spot for service or repair. Again, if the option is to just add another conduit for data or fire alarm and be separate, i would definately do it.
In oregon, the system would have to be installed by an electrician with at least a class A Limited Energy License, and ideally by someone with minimum of NICET level 1 certification.
your mileage may vary.