brushfunk1
Vendor
I have a situation using plenum systimax cat 6 used for furniture feeds that is stubbed into the deck of a building. There looks to be some water in the slab pipe. Head of pull was taped up and at least 15 feet was cut off. Upon termination noticed moisture inside cable jacket. Time from install to termination and testing <4hours. No damage to jacket pulling. All failed/marginal pass return loss test. 5 other dry pipe feeds in slab all passed clean. I know my correct fix but it would involve re-piping below terrazzo Should I be concerned about initial performance and over time?