Is a ceiling grid wire considered a raceway according to the NEC 2008 edition? Is there a code (other than local) that exists that says J-hooks cannot be attached to ceiling grid wires?

"However beautiful the strategy, you should occasionally look at the results." Sir Winston Churchill
 
I do not know of any "codes" that state this. But it does not go along with the "standards" set by TDMM or the ITSI set by BICSI.

When is the last time you helped someone, just because you were able to?

For the best response to a question, read faq690-6594


 
You might want to have a look at 2005 NEC Article 300 Wiring Methods:
300.4 Protection against physical damage.
300.11 Securing and Supporting.

2005 NEC Article 800 Communications Circuits:
800.24 Mechanical Execution of Work.
800.133 Installation of Communication Wires, Cables, and Equipment: Support of Conductors.
800.154 Applications of Listed Communications Wires and Cables and Communications Raceways.

These sections of the 2005 or later editions of NEC should cover your area of concern.

If you want a short summary of examples of these types of installs, get a copy of the ERICO CADDY Electrical and Low Voltage/Datacom Fasteners catalogue 2007-2008 or later. You may call them @ 800-252-2339 or erico.com.

Hope this helps!

....JIM...
 
This is primarily a Building Code issue, sorry I do not have a copy of that code to cite the actual code, but every jurisdiction I know of requires ceiling grid wires to be used ONLY to support ceiling grid.
You must install your own ceiling wires to use them to support anything other than the ceiling grid.
This became a bigger issue after the Loma Prieta earthquake in CA, and is generally rigidly enforced in most if not all jurisdictions.

Richard S. Anderson, RCDD
 
Serva and Syq are correct. You can run your own grid wires but you cannot use the existing ceiling grid, ever.

Regards
Peter Buitenhek
ProfitDeveloper.com

"Never settle for a job well done...always look for cost cutting measures
 
And that goes for "attaching cables to conduit" as a means of support! - One of the most violated codes around!

....JIM....
 
Found the code in NEC 300.11(A) Thanks for the guidance.