Need some help finding the following info in my OPT 11

- Line Build Out
- Switch Type
- Clocking Source

Reason, I'm having some challenges with clicking on a PRI and need to verify these setting to move forward.

THX.
 
do an slt at the req prompt in 22 and the header info should have switch info. the other items on an 11 someone else will have to post, i'm 11 ignorant.

Mato' Was'aka
 
I guess I should have clarified on the the Switch Type.
I mean how do I find out what the switch type setting is for the PRI... ie, Siemens, Nortel DSM.

Sorry.
 
prt you Dch in 22 look at ifc

REQ prt
TYPE adan dch xxx

Mato' Was'aka
 
Groovin' Gentlemen you've help me answer 2 of the 3 questions.

Now about "Line Build Out" If I rememeber correctly that's configured by the DIPS on the Daughter Board... Yes/ No?
 
are you talking about B8ZS and ESF?


>ld 22
PT2000

REQ prt
TYPE cequ

CEQU
MPED 8D
TERM
REMO
TERD
REMD
TERQ
REMQ
SUPL 004 028 N064 N068
N096
SUPC
SUPF
XCT 000 016
TDS * 000 * 016
CONF * 001 * 017
MFSD * 000 * 016

DLOP NUM DCH FRM TMDI LCMT YALM TRSH
PRI 020 24 ESF NO B8S FDL 00
021 24 ESF NO B8S FDL 00
022 24 ESF NO B8S FDL 00
023 24 ESF NO B8S FDL 00
MISP
EXT0 3PE
CNI 012 000 000
EXT1 3PE
CNI 012 000 000
MCFN S0B0 S0B1 S1B0 S1B1 S2B0 S2B1 S3B0 S3B1 FLSH TOTL
016 016 016 016 016 016 000 000 64 160





Thanks,

Buddy
 
On an NTAK09 DTI/PRI card there are 4 switches that allow for varying distances from Telco equipment demarc, this sits right in front of where the daughter boards would connect to the card. Manipulating these switches works like LBO settings.
 
can you see what the switches are set for via software or only physically looking at the DIPS?
 
They are physical switches that have to be manually set, to my knowledge there is no software you can look at that will tell you what it is set for
Opt 11 1.5Mb DTI/PRI Administration and Maintenance Guide has a table with the options. It is fairly straight forward.
 
That's what I thought, Thanks for confirmation.
 