Avaya UPS down

Status
Not open for further replies.

telecomadmin12

Technical User
Apr 27, 2012
406
DE
We have Avaya 8700 servers plugging into Avaya UPS units.
One UPS unit is no longer working after a power outage so we are wondering if we can just plug the 8700 server into a normal power outlet in the wall not using the UPS.
Will this work?

Also the 8700 manual says that upon installing the servers it must be "verified that the customer-provided AC power to the rack is from a nonswitched outlet".
Why is this important?
 
I'd say you can plug it in to an outlet. I believe that the switching means that a switch can't turn it off, aka -always on.
 
So you don't walk in the server room and flip off a light switch and turn off your servers!

Yeah, you can plug'em into 120AC. But, if they're old S8700s and not 8710s or 20s or 30s, then they're really old.

They're tanks. And I'll bet that the UPS's are isolating too so if you used something like a Fluke 1710 voltage logger, you'd see real clean stuff from the UPS-->servers and you could see awful garbage from the wall-->UPS

You can go straight to the wall if you don't mind gambling on your power quality vs your old power supplies!
 
most ups units can be put into bypass mode so this way it can still remained plugged into the ups.

ACSS IP Office AIPS IP Office
 
I have plugged the server directly into the wall and things are working.

Since the power outage I have major alarms, PKT-INT alarms, what do those mean?:

CommunicaMgr Alarms:
ID MO Source On Bd Lvl Ack Date
1 TONE-BD 01B y MIN Y Thu Apr 30 19:17:21 EDT 2020
2 PKT-INT 01B y MAJ Y Thu Apr 30 19:17:21 EDT 2020
3 PKT-INT 01B y MAJ Y Thu Apr 30 19:15:31 EDT 2020
4 SYS-LINK 01B0101 n MIN Y Thu Apr 30 19:15:21 EDT 2020
5 POWER 01 y MIN Y Thu Apr 30 19:12:59 EDT 2020
 
Code:
                       IP SERVER INTERFACE INFORMATION

Port Pri/   Primary/         Primary/         Primary/                State Of
Ntwk Sec    Secondary        Secondary        Secondary Serv  Control Health
Num  Bd Loc IP Address       Host Name        DHCP ID   State State   C P E G
---- ------ ---------------  ---------------- --------- ----- ------- -------
  1   1AXX  198.152.254.199  198.152.254.199  ipsi-A01a  IN   actv-aa 0.0.0.0
      1B01  198.152.255.199  198.152.255.199  ipsi-A01b  OUT  standby 0.1.0.0
 