hi guys,
I have remote lim with 2 magazinez, each time i reload that lim, the LPU disply stuck at 3230 and nothing happens after that, i tried changing HW but still samething, is it HW problem or GJUL-GJUG connection or backup problem?
plz advice
3230 is "good" in that both DSU's are seen in the remote lim (32) and that the I/O lim has made contact with the remote lim (30). Depending on the size of the system etc. it can take a few minutes or so before you see a "40" and loading begins....how long do you wait before you decide that nothing is happening?
It's quite possible that REM2 is hung...I have SACOP's for BC-9 & BC-11, but I dunno if the values in BC-12 have change from those in BC-11. I also don't know what release your system is.
The quick & dirty method is to poke lim1, but that's generally only as a last resort.
For dstrang1; addresses in REM2 are good for BC11 & BC12.
BC11 & BC12 addr = 1B2&1D0
3230 indicates the lim has two magazines and has contact
with the I/O lim. Next display should be just 40 which
says the lim has received a reload order from the I/O
lim. Next display after that = 70 then 71 then 8X's.
I think giving the variable name will be more clear than giving variable address, because maybe it is not the same for all AS.
1B0 CRELREUNIT
1B2 CREM2STATUS
1D0 CSTARTMODE