And how does a 655A in a G650 compare?
So, I found out a customer built their PBX out of spare parts including many TN2224B HV12 circuit packs. The ones that don't use their angel ID to set a delay in when they draw max current when the PN powers up. The ones that can overload the power supply. Some support information says >HV13 is ok, others say HV18. Either way, its not like they're getting more TN2224Bs.
So, I read that a 676B supply in a SCC should have no more than 1 TN2224B HV9-12 in a carrier. A 676C, <13, a WP-91153 <6. a 1217A <3. There must be something particular about how these power supplies start up.
I'm curious how a 655A in a G650 would factor into that equation.
I guess the whole angel-ID thing makes sense. Every time I saw a PN come up, it was always the IPSI and then "no board" all the way through and they would come up sequentially. Come to think of it, I almost want to say I remember seeing A02 and B02 and C02 coming up before A03 B03 and C03. I guess I'm just curious because I've never found out - or needed to find out - how a port network comes online in any significant detail. And what the heck about power supply type makes it that they can each supply max power to only a certain number of cards, and every power supply is different? I guess it's the sort of thing that doesn't need to be published if the cards are supposed to go one at a time. Anyhow, thought I'd ask
So, I found out a customer built their PBX out of spare parts including many TN2224B HV12 circuit packs. The ones that don't use their angel ID to set a delay in when they draw max current when the PN powers up. The ones that can overload the power supply. Some support information says >HV13 is ok, others say HV18. Either way, its not like they're getting more TN2224Bs.
So, I read that a 676B supply in a SCC should have no more than 1 TN2224B HV9-12 in a carrier. A 676C, <13, a WP-91153 <6. a 1217A <3. There must be something particular about how these power supplies start up.
I'm curious how a 655A in a G650 would factor into that equation.
I guess the whole angel-ID thing makes sense. Every time I saw a PN come up, it was always the IPSI and then "no board" all the way through and they would come up sequentially. Come to think of it, I almost want to say I remember seeing A02 and B02 and C02 coming up before A03 B03 and C03. I guess I'm just curious because I've never found out - or needed to find out - how a port network comes online in any significant detail. And what the heck about power supply type makes it that they can each supply max power to only a certain number of cards, and every power supply is different? I guess it's the sort of thing that doesn't need to be published if the cards are supposed to go one at a time. Anyhow, thought I'd ask