Hi,
OK. I just dropped by looking for advice in a somewhat technical question I found no better place to ask. There we go
Family business, managing a lottery and gambling office of a state company. Games/bets are served over a propietary computer/data network over ADSL, serviced using a propietary software system online terminal. Terminals must be kept online at all times...
And for convenience, we safeguard the terminal from power failures using a SAI (power outages while servicing transactions means stupid reporting downtimes; other critical operations benefit aswell). So it may be convenient and useful for us to run the terminal SAI powered when a blackout hits. Moreover, the SAI has no possibility of management.
You get the picture. Lots of deep cycles for the poor cheap lead-acid SAI... dead battery.
BTW, SAI is a Riello iDialog plus ID60 -600 VA-.
Using a standard automotive battery apparently fixes the deep cyclation/battery overload issue, due to much higher capacity. But if power outs when no-one is in the office... battery will still die, even if it takes 4 or 5 hours. With a blistering stated recharge time of 6-8 h for the puny 7 Ah standard battery, expect at least a couple days to get the big one back into full condition! lol
So I was wondering about the possibility of fitting a custom built Ni-MH to the SAI (no deep cycling issues thus).
Lets say, for example, a 10S6P (10 in series, 6 in parallel, 60 cell array) of 2600 MAh AAs.
Voltage range is 12 to 15 V. Nominal voltage is the same as in the lead batt, and peak voltage is high enough so no over-charging problems should arise (lead is usually charged to 2,4 or 2,45 V per cell, 14,4 - 14,7 V peak).
MFG (over)stated peak capacity 15,6 Ah. Let's say the battery is good for 12 Ah.
The UPS would, at most drain barely above 30 Amps at peak load. That means a 2,5C worst case scenario discharge rate. 1C discharge rate for typical operation. Should be handled easily by the cells.
OK. That's my idea. Now, if someone has something so say about UPS batt charging circuitry messing around here or there, or whatever... do it!
Thank you in advance.
Regards,
Barkuti
OK. I just dropped by looking for advice in a somewhat technical question I found no better place to ask. There we go
Family business, managing a lottery and gambling office of a state company. Games/bets are served over a propietary computer/data network over ADSL, serviced using a propietary software system online terminal. Terminals must be kept online at all times...
And for convenience, we safeguard the terminal from power failures using a SAI (power outages while servicing transactions means stupid reporting downtimes; other critical operations benefit aswell). So it may be convenient and useful for us to run the terminal SAI powered when a blackout hits. Moreover, the SAI has no possibility of management.
You get the picture. Lots of deep cycles for the poor cheap lead-acid SAI... dead battery.
BTW, SAI is a Riello iDialog plus ID60 -600 VA-.
Using a standard automotive battery apparently fixes the deep cyclation/battery overload issue, due to much higher capacity. But if power outs when no-one is in the office... battery will still die, even if it takes 4 or 5 hours. With a blistering stated recharge time of 6-8 h for the puny 7 Ah standard battery, expect at least a couple days to get the big one back into full condition! lol
So I was wondering about the possibility of fitting a custom built Ni-MH to the SAI (no deep cycling issues thus).
Lets say, for example, a 10S6P (10 in series, 6 in parallel, 60 cell array) of 2600 MAh AAs.
Voltage range is 12 to 15 V. Nominal voltage is the same as in the lead batt, and peak voltage is high enough so no over-charging problems should arise (lead is usually charged to 2,4 or 2,45 V per cell, 14,4 - 14,7 V peak).
MFG (over)stated peak capacity 15,6 Ah. Let's say the battery is good for 12 Ah.
The UPS would, at most drain barely above 30 Amps at peak load. That means a 2,5C worst case scenario discharge rate. 1C discharge rate for typical operation. Should be handled easily by the cells.
OK. That's my idea. Now, if someone has something so say about UPS batt charging circuitry messing around here or there, or whatever... do it!
Thank you in advance.
Regards,
Barkuti