I'm trying to setup remote call forward and am having difficulty assigning a Station Control Password. The error I'm getting is 'SCH8889 CEPT default does not match the password defined in LD15'. What do I need to setup in LD15 to continue past this error message?

Thanks.
 
Check your settings first in LD 21. Use "FFC" as the gate opener to list out your current "SCPL". It may be set to "0".

Go into LD 15

Go & change "FFC". Scroll down until you see SCPL. Put in the required number of digits (Usually to match the systems DN digit length!).
You may well get a "SCH" error code, Informing you that the change will become activated after a system reload!.
If that is the case, Then do a "EDD" in LD 43 first.

e.g.

FFC_DATA
CCRS TLD
SCPL 4 ------ Set to 4 digits
SBUP YES
FFCS NO
STRL 0
STRG
ADLD 0

I hope this helps.

All the best

Firebird Scrambler
Meridian Programmer in the UK
 
the pwd you are using is the wrong length
the length is set in LD 15

try printing in LD 21 gate opener FFC
then look for the SCPL prompt, that tells you the length of SCPW


Colin
 