Servers with Dual PSU being fed from 2 phases / UPS

Status
Not open for further replies.

MrJibbles

MIS
Apr 25, 2007
2
0
0
GB
Hi,
Just seeing if there are any issues with running servers which have dual psu installed from different phases from one UPS or a different phase from another ups?
Thanks in advance
Giles
 
No problem at all. But it is better practice, if you have more than one UPS to power each server's power supply from different UPS, just for redundancy.



___________________________________
Joe
Electro-mechanic Engineering
jpm@ieee.org
 
Mr Jibbles -
If it is possible, you DO want to run the redundant Power supplies from different AC sources. Definitely not from the same outlet or wall circuit, preferably from a differnt circuit breaker in your power panel, and if possible from a different power company circuit supplying power to your building. I was in a high rise once where the building had access to completely different power grids - an unusual situation. If you're running a Data Center size UPS, it doesn't matter that much, but if you're running individual UPS's, it's nice to improve your odds that if power to one UPS fails, power to the other won't have failed at the same time. You're protecting yourself against local power interruptions - secretaries plugging in too many electric heaters and popping a breaker, facilities staff plugging in a floor buffer where they shouldn't, etc.

Fred Wagner

 