"...If you run cable in the plenum, the area above the ceiling tile or below th subflooring, make sure the cable sheath is PLENUM-RATED [the plenum was my mistake] and consult with local electric installation codes to be certain you are installing it correctly. A plenum-rated cable is more fire-resistant than other cables and its sheath will not release noxious fumes if it does start to burn..."
Well thanks for quoting, i wasn't picking on your plenum or plenum rated terminology, just that the statement is incorrect. And man I just can't complain about your effort, you bought a book and read it! Unfortunately, the author did not do a very good job of explaining the details. I'm not familiar with the book or the author, always a good idea to find out if the author has actually done this type of work and what his/her background is.
The National Electrical Code 2002 Article 100 defines Plenum thusly: "A compartment or chamber to which one or more air ducts are connected and that forms part of the air distribution system." The NEC Article 800.53(A) says (A) "Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be type CMP."
Now, in residential construction for example, often they select a stud bay, the void between two studs in wall to be a vertical plenum to get return air from one floor to the next. They usually paint that stud bay and we can't run wire through there unless it is plenum rated.
In commercial type construction, there are some common misconceptions. If there is a drop ceiling in place, that is NOT necessarily an idication that the space above it is a plenum space. IF you look above the tile and there are heading ducts AND return air ducts, then the environmental air is contained in that duct work, and that area above the tile is not a plenum space.
The same goes for raised floors, if they are ducting the air in and out, it isn't a plenum space.
One example of these types of space that we run into are some schools where there are 'tunnels' under the school hallways that contain piping. At many of them, there is a large air handler that pressurizes the entire tunnel area, and they have ducts and vents going to the classrooms. It's similar to a wind tunnel when the heater is running, but THAT area is all plenum space, anthing in that space needs to be plenum rated.
Hopefully that makes sense. Simply, if they are moving environmental air (HVAC breathing air, forced or return) through the space in question, you need plenum rated material.
This book looks like it covers the Net+ material from someone who has probably never been in the field and pulled wire. I would recommend if you are looking for cabling books, look for those by people who do cabling. This book appears to be a 'how to pass the NET+ exam' type book. Not the greatest reviews on Amazon. Sorry, it's frustrating when there is misinformation in something this widespread, but it looks like she missed the boat in a lot of areas. If i wasn't so busy, i'd get the book and challenge her on her mistakes
good luck!
Daron J. Wilson, RCDD