Those "on board y" alarms will only clear when the hardware issues are resolved
Basic tier 1 troubleshooting methods can be used.
G650 cabinets with 655 power supplies in slot 00 and slot 15 are redundant (active/standby)
They can be changed hot without affecting service in the cabinet.
Moving them between cabinets and swapping them with other 655 that are not alarmed can
tell you a lot.
almclear -a does not clear active hardware alarms.
-------------------------------------------------------------------------------
Alarms reported for CM are used for information:
Maintenace Object
on board - y/n
Alarm Type - MAJOR/MINOR/WARNING
Svc State
Ack 1 2 - Did the alarm receivers get notified and send back Acknowledgement
Date Alarmed Timestamp
Date Resolved Timestamp
--------------------------------------------------------------------------------
display errors hi
This will help you with what to look up in the Avaya Maintenance Documentation to
further investigate failing hardware and steps for resolution
Code:
list configuration power-supply 2
list configuration power-supply 3
list configuration power-supply 4
status environment 2
status environment 3
status environment 4
test environment 2 long
test environment 3 long
test environment 4 long
list configuration power-supply 1
SYSTEM CONFIGURATION - 655A Power Supplies
Power Supply Power Supply Power Supply
Location Serial Number Make/Model Number SAP Firmware Version
01A00 05R411001355 Power Unit 655A Rev B 700246671 2.19A
01A15 09DT37285471 Power Unit 655A Rev 00 700460041 1.12
01B00 05R411000509 Power Unit 655A Rev B 700246671 2.19A
--------------------------------------------------------------------------------
status environment 1
CABINET POWER SUPPLY STATUS (655A)
Pow Alm Temp(F/C) Hot Voltage FAN Ring Voltage Input
Loc Cnt InLet Exhst Spot +5 -5 -48 Ctrl Alm Stat Ctrl Set Det Power
01A00 0 71/22 71/22 ok 5.15 5.15 49.0 mid N ok actv 20HZ Y AC
01A15 3 71/22 69/21 ok 5.10 5.13 49.0 mid N ok stby 20HZ Y -
01B00 0 68/20 71/22 ok 5.10 5.10 48.8 mid N ok actv 20HZ Y AC
--------------------------------------------------------------------------------
test environment 1 Page 1
TEST RESULTS
Port Maintenance Name Alt. Name Test No. Result Error Code
01 CAB-EXFR 1532 PASS
01 CAB-PFL 1533 FAIL
01 SER-BUS 1531 PASS
01A00 POW-SUP 1535 PASS
01A00 POW-SUP 1536 PASS
01A00 POW-SUP 1649 PASS
01A00 CAB-TEMP 1537 PASS
01A00 CAB-TEMP 1538 PASS
01A00 PS-RGEN 1540 PASS
01A15 POW-SUP 1535 FAIL 12
01A15 POW-SUP 1536 PASS
01A15 POW-SUP 1649 FAIL 1
01A15 CAB-TEMP 1537 PASS
01A15 CAB-TEMP 1538 PASS
01A15 PS-RGEN 1540 PASS
01B00 POW-SUP 1535 PASS
01B00 POW-SUP 1536 PASS
01B00 POW-SUP 1649 PASS
01B00 CAB-TEMP 1537 PASS
01B00 CAB-TEMP 1538 PASS
01B00 PS-RGEN 1540 PASS
A great teacher, does not provide answers, but methods to teach others "How and where to find the answers"
bsh
40 years Bell, AT&T, Lucent, Avaya
Tier 3 for 30 years and counting
[URL unfurl="true"]http://bshtele.com[/url]