Where did you get this idea? "
It borders on gnit picking, but one of several places ...
......................
NEC 250.24 Grounding and Bonding at Service Equipment
4) Main Bonding Jumper. When the grounded neutral conductor is bonded to the service disconnecting means [250.24(B)] by a bus bar [250.28], the grounding electrode conductor can terminate to either the grounded neutral terminal or the equipment grounding terminal within the service disconnect.
......................
Neutral-to-Ground Bonding: Not An Option
The National Electrical Code® explicitly
defines grounded conductors and grounding
conductors as follows: A grounded conductor is
the wire common to all phases in a multi-phase
system. This conductor is more commonly
known as the system neutral conductor.
A grounding conductor is the grounding
electrode for the multi-phase electrical system.
This is the conductor most often referred to as
the ground conductor.
Article 250-26 discusses the grounding of a
separately derived alternating current system and
states that “…a bonding jumper shall be used to
connect the equipment grounding conductor of
the derived system to the grounded conductor.
This connection shall be made at any point on
the separately derived system or at the source of
a system that has no disconnecting means or
overcurrent devices. The intent of this section is
to permit this connection at the transformer.”
Why is a missing bond a problem?
If a short occurs between a phase and ground
without the presence of a neutral-to-ground bond
at the upstream transformer, the distribution
system’s neutral conductor will “float” or lose its
reference to ground. The floating neutral
condition can cause voltages to float to a
maximum of 208 volts RMS relative to ground,
subjecting loads to a sustained overvoltage
condition.
Even if one assumes light or balanced loading,
the electrical distribution system may operate
without any apparent side effects for quite some
time. Should the loading become unbalanced or
an electrical short occur, the phase voltages will
fluctuate severely.
How does sustained overvoltage
cause problems with SPDs?
Most SPD manufacturers include 25 percent
“headroom” in their products to accommodate
normal voltage fluctuations routinely generated
by the local utility provider. By utilizing 150
Vrms MOVs (metal oxide varistors), the device
should be safe from the 10 percent voltage
deviation a utility is likely to produce.
However, any voltage exceeding the value would
cause the components to conduct. The
continuous conduction is what the SPD
components are not designed to handle.
This condition is what causes the majority of
SPD failures as explained by Dr. Francois
Martzloff in his article “What Are the Lights on
Your Surge Protector Telling You?” (Power
Quality Assurance, July 1998).* Recently, a
major printing plant and high school (which used
different electrical contractors) reported their
SPDs had failed during installation. Upon
visiting the sites, engineers quickly discovered
the problem. In both cases, the neutral-to-ground
bond was not made at the transformers. A short
occurred that caused at least two phases to
encounter sustained overvoltages in excess of
150 Vrms.
It is very important to know that this short would
have occurred regardless of the type of SPD
product or particular manufacturer. That’s
because the MOVs (metal oxide varistors) used
in SPDs are designed to share current at the
microsecond time frame – and not to survive
sustained overvoltages.
The amazing thing is that the electricians for the
school and the printing plant were unaware that
the NEC requires establishing the neutral-ground
bond on the secondary side of the transformer.
The Neutral to Ground Bond
NEC 250-2x
Where is it NEC compliant to bond neutral
and ground? The NEC prescribes two
places. The first place that we find this bond
is at the service entrance inside the main
service panels. Why? Fault current at this
point needs to come from the utility source.
The other place where the neutral and ground
are required to be bonded is on the secondary
side of what the NEC calls a "separately
derived system." The most common separately
derived system is a power transformer
where the primary and secondary windings
are galvanically isolated from one another.
This describes the NEMA-type transformer
widely used to distribute power inside all commercial
buildings.