Hi Guys
I have this alarm comming in " 60 Fault code without alarm class" ALP 1 NOIF 1 unit ALR EQU 001++++ INFI 782"
I think it may be the CIL data unit or computer connected to that but am not sure the cil data is off Lim 2 and it looks like it maybe @ lim 1?
two questions 1. what is it
2. how do I put an alarm class on it and explantion.
Many thanks for your help in advance.
Cheers Brian

Cheers Brian
To see is to know To Know is to see
 
Hi,
ADD INFO 1 contains the relevant fault code.
Here it's 782 which is an external source alarm, so at the ALU input 1-x-xx-x there must be an entry which is short-circuited.
 
Hi Mundus many thanks I will be there on Monday so will see what I can find
Cheers Brian