fault code 84 1

Status
Not open for further replies.

klobo1970

IS-IT--Management
Feb 10, 2016
9
0
0
HR
DATE: 10FEB16 TIME: 11:25:53
CLASS: 4
84 UNDEFINED ALARM BOARD INPUT ACTIVATED
DATE TIME ALP NOIF EQU BRDID INF1
10FEB16 10:19:07 1 1 001-0-40-00 19 7

i dont understand description of alarm in ALEX

please help...thanx
 
You have an ALU board in position 001-0-40-00 and one of the external alarm inputs (ALI 7) has been activated but is not defined by command ALEII, ALAII or ALSII. Confirm this with ALEXP;

Typical external inputs are from an equipment room door alarm or from an air conditioning unit.
Check to see what the input is wired to and define it with the appropriate command. Alternatively, remove the input if not in use.
 
<ALEXP;
EXTERNAL ALARM DATA
BPOS: 1-0-40
NO INPUTS ASSIGNED
NO OUTPUTS ASSIGNED

i think i remove the input, i dont think it is in use

thanx in advice
 