YOUNG_BLOOD

Systems Engineer
Oct 31, 2017
1
US
Hi Everyone

Please can you assist. I am trying to get control of a system we have onboard our Yacht after a disagreement with the company that it installed it some 9 years ago. I have found all of the software online and installed it ( and I can connect using the serial cable and the bpinspect tool but cannot get the BMS server to connect so that I can regain control of our system.

1.) I have no passwords so will I even be able to get into the system without these?
2.) How do i verify what BMS software is correct for my BP250? I am assuming the latest software version will work with all hardware versions?
3.) Is there a way to transfer a config file from bpinspect to the BMS server to load the correct configuration? I cannot get the serial connection to connect.
4.) My systems serial number ends in R4A. Is this the version number?
5.) By all accounts it seems as though licensing is now offered free for this software. I am yet to try the license key but shall do so now and see if this helps (install as standard key I am assuming).

Apologies in advance if I sound like a newbie but I have substantial knowledge with Panasonic PBX systems and only now getting in touch with my vintage Ericsson/Aastra side!! :)

All the Best

[pc3][afro2]
 
OK, won't be easy...maybe even not possible, but let's try...
1. Without password - not possible to connect. Try with default password - 33333
2. On BP CPU card (first card from the left) - do you have CF disk or you have FECU (Black box connected to the front of CPU)? If FECU - post what is on the sticker
3. BP Inspect is not backup tool - it's been used only fault tracing and some other actions - nothing to transfer there
4. Irrelevant - this is (usually) only HW revision of the cards (but could be revision of initially loaded SW version)
5. Yes, install as Standard key - but even without License you still should be able to connect (with only few commends visible but connectivity is not affected)
You can also access to the system via digital phone (DBC 213, 214, DBC 223 or 224) with lower level of passwords (22222, 11111)but not all commends are available (and no change of top level password). If all fail, "cold" start is your only option (system default) and start from beginning. Looking on where system is installed (environment)- would be fairly easy to get everything up and running
 